control path with differnent rise and fall characteristics

Hi everyone,

I'm new to this group, hope someone can help me with this:

I need to model a control path with different rise and fall time. Both rise and fall time can be modelled as PT1[1], but with a Time constant of T1= 70ms on rise time and T2=150 on fall time.

Can anyone give me a tip how to model this in an LTI - System? Can it be modelled anyway?

many thanks in advance, richard

[1] I hope this is also called PT1 in english: U = Uo * (1-exp(t/T))
Reply to
richard bruckner
Loading thread data ...

There is a unit delay function, which for a specified time delay, say d, would allow you to write something like this:

U = Uo * (1-exp(t/T1) - (Uo(t-d))*exp(t/T2) ...... where Uo(t-d) is directly transformable.

How does this relate to your application?

Dave

Reply to
David Corliss

I haven't seen the 'PT1' notation; I'm not sure where it's from.

This cannot be modeled exactly as a linear time invariant system, so the question you need to ask isn't "how do I model this", but "can do I model this _well enough_ to match _my environment_, and how". This means that you have to make a realistic assessment of your needs and your environment, because you can kill yourself both by being too optimistic and too pessimistic.

You speak of separate rise and fall times -- is this system actuated by an on/off actuator? If your actuator isn't proportional then the system cannot, by definition, be truly LTI. If it's on/off and you're using PWM to linearize it then you can close one eye and pretend it's a linear system, except then you have that 2x difference in apparent time constants to deal with.

Tell me more if I'm off base, but I'm going to assume it's something akin to your PWM'd on/off system with two distinctly different time constants, and rattle out some approaches:

The linearized (with PWM) system will have an effective time constant that ranges between 70ms and 150ms depending on the duty cycle. You could just model the system as having a time constant that ranges between these two values, and design a controller that's robust to the changes. If you're using classical control techniques then you should be OK with Bode and Nyquist plots of both extremes, possibly backed up with some root-locus plots of the final system as the time constant varies. I'd cling to this approach for a long time before I tried another.

You can use describing function analysis. In a sense this is what you've done already with step functions, and you've gotten two different answers. So if you do it with sine waves, i.e. stuff a sine wave into the input of your plant and look at the amplitude and phase of the fundamental of the output, then you may get something that's more representative.

You may be able to linearize the system by identifying the root cause of the time constant and controlling to that. I have built virtual torque drives for motors that measured the motor velocity, calculated the motor's back-EMF, and controlled the motor's voltage to get a certain current, all without actually measuring the motor current. This was in a system that could stand substantial inaccuracy, but it worked well enough*.

In your case you would look at what your actuator actually pushes on, and what actually pushes back to generate the two time constants. Then you'd work backward to whatever internal force is acting on the integrating element, and have a nonlinear feedforward to control the drive to that integrating element. This kind of thing can be astoundingly sensitive to plant variation though, so I wouldn't try it unless you know your system can stand the variation as the plant changes, or you _know_ you can avoid it in the first place.

  • I think "it works well enough" should be the catchphrase for all control systems designers, by the way -- you could kill off entire companies if everyone were chasing "optimum" instead of "good enough". I choose to think of it as "optimized for profit".
Reply to
Tim Wescott