Siemens S7-200 user guide: Prerequisites

Published by Siemens · pages 399–424 of 554 · Original PDF

8 discussions about the Siemens S7-200

All 22 parts of the user guide

Prerequisites

The loop that you want to auto-tune must be in automatic mode. The loop output must be controlled by the execution of the PID instruction. Auto-tune will fail if the loop is in manual mode.

Before initiating an auto-tune operation your process must be brought to a stable state which means that the PV has reached setpoint (or for a P type loop, a constant difference between PV and setpoint) and the output is not changing erratically.

Ideally, the loop output value needs to be near the center of the control range when auto-tuning is started. The auto-tune procedure sets up an oscillation in the process by making small step changes in the loop output. If the loop output is close to either extreme of its control range, the step changes introduced in the auto-tune procedure may cause the output value to attempt to exceed the minimum or the maximum range limit.

If this were to happen, it may result in the generation of an auto-tune error condition, and it will certainly result in the determination of less than near optimal suggested values.

Auto-Hysteresis and Auto-Deviation

The hysteresis parameter specifies the excursion (plus or minus) from setpoint that the PV (process variable) is allowed to make without causing the relay controller to change the output. This value is used to minimize the effect of noise in the PV signal to more accurately determine the natural oscillation frequency of the process.

If you select to automatically determine the hysteresis value, the PID Auto-Tuner will enter a hysteresis determination sequence. This sequence involves sampling the process variable for a period of time and then performing a standard deviation calculation on the sample results.

In order to have a statistically meaningful sample, a set of at least 100 samples must be acquired. For a loop with a sample time of 200 msec, acquiring 100 samples takes 20 seconds. For loops with a longer sample time it will take longer. Even though 100 samples can be acquired in less than 20 seconds for loops with sample times less than 200 msec, the hysteresis determination sequence always acquires samples for at least 20 seconds.

Once all the samples have been acquired, the standard deviation for the sample set is calculated. The hysteresis value is defined to be two times the standard deviation. The calculated hysteresis value is written into the actual hysteresis field (AHYS) of the loop table.

Tip While the auto-hysteresis sequence is in progress, the normal PID calculation is not performed. Therefore, it is imperative that the process be in a stable state prior to initiating an auto-tune sequence. This will yield a better result for the hysteresis value and it will ensure that the process does not go out of control during the auto-hysteresis determination sequence.

The deviation parameter specifies the desired peak-to-peak swing of the PV around the setpoint. If you select to automatically determine this value, the desired deviation of the PV is computed by multiplying the hysteresis value by 4.5. The output will be driven proportionally to induce this magnitude of oscillation in the process during auto-tuning.

Auto-Tune Sequence

The auto-tuning sequence begins after the hysteresis and deviation values have been determined. The tuning process begins when the initial output step is applied to the loop output.

This change in output value should cause a corresponding change in the value of the process variable. When the output change drives the PV away from setpoint far enough to exceed the hysteresis boundary a zero-crossing event is detected by the auto-tuner. Upon each zero crossing event the auto-tuner drives the output in the opposite direction.

The tuner continues to sample the PV and waits for the next zero crossing event. A total of twelve zero-crossings are required to complete the sequence. The magnitude of the observed peak-to-peak PV values (peak error) and the rate at which zero-crossings occur are directly related to the dynamics of the process.

Early in the auto-tuning process, the output step value is proportionally adjusted once to induce subsequent peak-to-peak swings of the PV to more closely match the desired deviation amount. Once the adjustment is made, the new output step amount is written into the Actual Step Size field (ASTEP) of the loop table.

The auto-tuning sequence will be terminated with an error, if the time between zero crossings exceeds the zero crossing watchdog interval time. The default value for the zero crossing watchdog interval time is two hours.

Figure 15-1 shows the output and process variable behaviors during an auto-tuning sequence on a direct acting loop. The PID Tuning Control Panel was used to initiate and monitor the tuning sequence.

Notice how the auto-tuner switches the output to cause the process (as evidenced by the PV value) to undergo small oscillations. The frequency and the amplitude of the PV oscillations are indicative of the process gain and natural frequency.

Figure from the manual

Figure 15-1 Auto-Tuning Sequence on a Direct Acting Loop

Based upon the information collected about the frequency and gain of the process during the auto-tune process, the ultimate gain and ultimate frequency values are calculated. From these values the suggested values for gain (loop gain), reset (integral time) and rate (derivative time) are calculated.

Tip Your loop type determines which tuning values are calculated by the auto-tuner. For example, for a PI loop, the auto-tuner will calculate gain and integral time values, but the suggested derivative time will be 0.0 (no derivative action).

Once the auto-tune sequence has completed, the output of the loop is returned to its initial value. The next time the loop is executed, the normal PID calculation will be performed.

PID Auto-Tune and the PID Tuning Control Panel Chapter 15

Exception Conditions

Three warning conditions can be generated during tuning execution. These warnings are reported in three bits of the ASTAT field of the loop table and, once set, these bits remain set until the next auto-tune sequence is initiated.

Warning 0 is generated if the deviation value is not at least 4X greater than the hysteresis value. This check is performed when the hysteresis value is actually known, which depends upon the auto-hysteresis setting.

Warning 1 is generated if there is more than an 8X difference between the two peak error values gathered during the first 2.5 cycles of the auto-tune procedure.

Warning 2 is generated if the measured average peak error is not at least 4X greater than the hysteresis value.

In addition to the warning conditions several error conditions are possible. Table 15-3 lists the error conditions along with a description of the cause of each error.

Table 15-3 Error Conditions during Tuning Execution \begin{tabular}{|l|l|} \hline Result Code (in ARES) & Condition \ \hline 01 aborted by user & EN bit cleared while tuning is in progress \ \hline 02 aborted due to a zero-crossing watchdog timeout & Half-cycle elapsed time exceeds zero-crossing watchdog interval \ \hline 03 aborted due to the process out-of-range & PV goes out-of-range: \newline \textbullet{} during the auto-hysteresis sequence, or \newline \textbullet{} twice before the fourth zero-crossing, or \newline \textbullet{} after the fourth zero crossing \ \hline 04 aborted due to hysteresis value exceeding maximum & User-specified hysteresis value, or automatically determined hysteresis value > maximum \ \hline 05 aborted due to illegal configuration value & The following range checking errors: \newline \textbullet{} Initial loop output value is < 0.0 or > 1.0 \newline \textbullet{} User-specified deviation value is <= hysteresis value, or is > maximum \newline \textbullet{} Initial output step is <= 0.0 or is > maximum \newline \textbullet{} Zero-crossing watchdog interval time is < minimum \newline \textbullet{} Sample time value in loop table is negative \ \hline 06 aborted due to a numeric error & Illegal floating point number or divide by zero encountered \ \hline 07 PID instruction was executed with no power flow (manual mode) & PID instruction executed with no power flow while auto-tuning is in progress or is requested \ \hline 08 auto-tuning allowed only for P, PI, PD, or PID loops & Loop type is not P, PI, PD, or PID \ \hline \end{tabular}

Notes Concerning PV Out-of-Range (Result Code 3)

The process variable is considered to be in-range by the auto-tuner if its value is greater than 0.0 and less than 1.0.

If the PV is detected to be out-of-range during the auto-hysteresis sequence, then the tuning is immediately aborted with a process out-of-range error result.

If the PV is detected to be out-of-range between the starting point of the tuning sequence and the fourth zero-crossing, then the output step value is cut in half and the tuning sequence is restarted from the beginning. If a second PV out-of-range event is detected after the first zero-crossing following the restart, then the tuning is aborted with a process out-of-range error result.

Any PV out-of-range event occurring after the fourth zero-crossing results in an immediate abort of the tuning and a generation of a process out-of-range error result.

S7-200 Programmable Controller System Manual

PID Tuning Control Panel

STEP 7-Micro/WIN includes a PID Tuning Control Panel that allows you to graphically monitor the behavior of your PID loops. In addition, the control panel allows you to initiate the auto-tune sequence, abort the sequence, and apply the suggested tuning values or your own tuning values.

To use the control panel, you must be communicating with an S7-200 PLC and a wizard-generated configuration for a PID loop must exist in the PLC. The PLC must be in RUN mode for the control panel to display the operation of a PID loop. Figure 15-2 shows the default screen for the control panel.

Figure from the manual

Figure 15-2 PID Tuning Control Panel

The control panel displays the station address (Remote Address) of the target PLC at the top left-hand side of the screen. At the top right-hand side of the screen, the PLC type and version number are displayed. Underneath the Remote Address field is a bar chart representation of the process variable value along with both it's scaled and unscaled values. Just to the right of the PV bar chart is a Current Values region.

In the Current Values region, the values of the Setpoint, Sample Time, Gain, Integral time, and Derivative time are displayed. The value of the Output is displayed in a horizontal bar chart along with its numerical value. To the right of the Current Values region is a graphical display.

The graphical display shows color coded plots of the PV, SP, and Output as a function of time. The PV and SP share the same vertical scale which is located at the left hand side of the graph while the vertical scale for the output is located on the right hand side of the graph.

At the bottom left hand side of the screen is the Tuning Parameters (Minutes) region. Inside this region, the Gain, Integral Time and Derivative Time values are displayed. Radio buttons indicate whether the Current, Suggested or Manual values for Gain, Integral Time and Derivative Time are being displayed. You may click on the radio button to display any one of the three sources for these values. To modify the tuning parameters, click the manual radio button.

You can use the Update PLC button to transfer the displayed Gain, Integral Time and Derivative Time values to the PLC for the PID loop that is being monitored. You can use the Start Auto Tune button to initiate an auto-tuning sequence. Once an auto-tuning sequence has started, the Start Auto Tune button becomes a Stop Auto Tune button.

Directly underneath the graphical display is a Current PID selection region with a pull down menu that allows you to select the PID loop that you wish to monitor with the control panel.

In the Sampling Rate region you can select the graphical display sampling rate from 1 to 480 seconds per sample. You can edit the sampling rate, then use the Set Time button to apply the change. The time scale of the graph is automatically adjusted to best display the data at the new rate.

You can freeze the graph by pressing the Pause button. Press the Resume button to resume sampling data at the selected rate. To clear the graph, select Clear from the right-mouse button within the graph.

388

To the right of the Chart Options region is a Legend that identifies the colors used to plot the PV, SP, and Output values.

Directly beneath the Current PID selection region is an area that is used to display information pertinent to the operation being performed.

The Advanced ... button in the Tuning Parameters region allows you to further configure parameters for the auto-tuning process. The advanced screen is shown below in Figure 15-3.

From the advanced screen you can check the box that will cause the auto-tuner to automatically determine the values for the Hysteresis and Deviation (default setting) or you can enter the values for these fields that minimize the disturbance to your process during the auto-tune procedure.

In the Other Options region you can specify the initial output step size and enter the zero crossing watchdog timeout period.

Figure from the manual Figure 15-3 Advanced Parameters

In the Dynamic Response Options region click the radio button that corresponds to the type of loop response that you wish to have for your process. Depending upon your process a fast response may have overshoot and would correspond to an underdamped tuning condition. A medium speed response may be on the verge of having overshoot and would correspond to a critically damped tuning condition. A slow response may not have any overshoot and would correspond to an overdamped tuning condition. A very slow response may not have overshoot and would correspond to a heavily overdamped tuning condition.

Once you have made the desired selections, click OK to return to the main screen of the PID Tuning Control Panel.

Once you have completed the auto-tune sequence and have transferred the suggested tuning parameters to the PLC, you can use the control panel to monitor your loop's response to a step change in the setpoint. Figure 15-4 shows the loop's response to a setpoint change (12000 to 14000) with the original tuning parameters (before running auto-tune).

Notice the overshoot and the long, damped ringing behavior of the process using the original tuning parameters.

Figure from the manual Figure 15-4 Response to a Setpoint Change

Figure 15-5 shows the loop’s response to the same setpoint change (12000 to 14000) after applying the values determined by the auto-tune process using the selection for a fast response. Notice that for this process there is no overshoot, but there is just a little bit of ringing. If you wish to eliminate the ringing at the expense of the speed of response, you need to select a medium or a slow response and re-run the auto-tuning process.

Once you have a good starting point for the tuning parameters for your loop, you can use the control panel to tweak the parameters. Then you can monitor the loop's response to a setpoint change. In this way you can fine tune your process for an optimum response in your application.

Figure from the manual

Figure 15-5 Response after Auto-Tune Process

390

Technical Specifications

In This Chapter

  • General Technical Specifications ........ 392
  • CPU Specifications ........ 396
  • Digital Expansion Modules Specifications ........ 405
  • Analog Expansion Modules Specifications ........ 412
  • Thermocouple and RTD Expansion Modules Specifications ........ 424
  • EM 277 PROFIBUS-DP Module Specifications ........ 438
  • EM 241 Modem Module Specifications ........ 450
  • EM 253 Position Module Specifications ........ 452
  • (CP 243-1) Ethernet Module Specifications ........ 458
  • (CP 243-1 IT) Internet Module Specifications ........ 460
  • (CP 243-2) AS-Interface Module Specifications ........ 463
  • Optional Cartridges ........ 465
  • I/O Expansion Cable ........ 466
  • RS-232/PPI Multi-Master Cable and USB/PPI Multi-Master Cable ........ 467
  • Input Simulators ........ 471

Figure from the manual

General Technical Specifications

Standards Compliance

The national and international standards listed below were used to determine appropriate performance specifications and testing for the S7-200 family of products. Table A-1 defines the specific adherence to these standards.

  • European Community (CE) Low Voltage Directive 73/23/EEC
    EN 61131-2:2003 Programmable controllers - Equipment requirements

  • European Community (CE) EMC Directive 89/336/EEC
    Electromagnetic emission standard
    EN 61000-6-3:2001 residential, commercial, and light industry
    EN 61000-6-4:2001 industrial environment
    Electromagnetic immunity standards
    EN 61000-6-2:2001 industrial environment

  • European Community ATEX Directive 94/9/EC
    EN 60079-15 Type of protection ‘n’
    ATEX Directive applies to CPUs and expansion modules with a rated voltage of 24 VDC. It does not apply to modules with AC power systems or Relay outputs.

After July 2009, the following applies:

  • EC Directive 2006/95/EC (Low Voltage Directive) “Electrical Equipment Designed for Use within Certain Voltage Limits”
    EN 61131-2:2007 Programmable controllers - Equipment requirements and tests

  • EC Directive 2004/108/EC (EMC Directive) “Electromagnetic Compatibility”
    EN 61000-6-4:2007: Industrial Environment
    EN 61131-2:2007: Programmable controllers - Equipment requirements and tests

  • EC Directive 94/9/EC (ATEX) “Equipment and Protective Systems Intending for Use in Potential Explosive Atmospheres”
    EN 60079-15:2005 Type of protection ‘n’

The CE Declaration of Conformity is held on file available to competent authorities at:

Siemens AG
IA AS RD ST PLC Amberg
Werner-von-Siemens-Str. 50
D92224 Amberg
Germany

  • Underwriters Laboratories, Inc.: UL 508 Listed (Industrial Control Equipment), Registration number E75310

  • Canadian Standards Association: CSA C22.2 Number 142 (Process Control Equipment)

  • Factory Mutual Research: Class Number 3600, Class Number 3611, FM Class I, Division 2, Groups A, B, C, & D Hazardous Locations, T4A and Class I, Zone 2, IIC, T4.

Tip
The SIMATIC S7-200 series meets the CSA standard.
The cULus logo indicates that the S7-200 has been examined and certified by Underwriters Laboratories (UL) to standards UL 508 and CSA 22.2 No. 142.

Technical Specifications Appendix A

Maritime Approvals

The S7-200 products are periodically submitted for special agency approvals related to specific markets and applications. This table identifies the agency and certificate number that the S7-200 products have been approved for. Most S7-200 products in this manual have been approved for these special agency approvals. Consult your local Siemens representative if you need additional information related to the latest listing of exact approvals by part number.

\begin{tabular}{|l|l|} \hline Agency & Certificate Number \ \hline Lloyds Register of Shipping (LRS) & 99 / 20018(E1) \ \hline American Bureau of Shipping (ABS) & 01-HG20020-PDA \ \hline Germanischer Lloyd (GL) & 12 045 - 98 HH \ \hline Det Norske Veritas (DNV) & A-8862 \ \hline Bureau Veritas (BV) & 09051 / B0BV \ \hline Nippon Kaiji Kyokai (NK) & A-534 \ \hline Polski Rejestr & TE/1246/883241/99 \ \hline \end{tabular}

Relay Electrical Service Life

The typical performance data supplied by relay vendors is shown in Figure A-1. Actual performance may vary depending upon your specific application. An external protection circuit that is adapted to the load will enhance the service life of the contacts.

2A Rating

10A Rating

Figure from the manual

Figure A-1 Relay Electrical Service Life

Technical Specifications

All S7-200 CPUs and expansion modules conform to the technical specifications listed in Table A-1.

Notice When a mechanical contact turns on output power to the S7-200 CPU, or any digital expansion module, it sends a "1" signal to the digital outputs for approximately 50 microseconds. You must plan for this, especially if you are using devices which respond to short duration pulses.

393

Figure from the manual

Table A-1 Technical Specifications

Environmental Conditions — Transport and Storage
EN 60068-2-2, Test Bb, Dry heat and EN 60068-2-1, Test Ab, Cold -40° C to +70° C
EN 60068-2-30, Test Db, Damp heat 25° C to 55° C, 95% humidity
EN 60068-2-14, Test Na, Temperature Shock -40° C to +70° C dwell time 3 hours, 2 cycles
EN 60068-2-32, Free fall 0.3 m, 5 times, product packaging
Environmental Conditions — Operating
Ambient Temperature Range (Inlet Air 25 mm below unit) 0° C to 55° C horizontal mounting, 0° C to 45° C vertical mounting 95% non-condensing humidity
Atmospheric pressure 1080 to 795 hPa (Corresponding to an altitude of -1000 to 2000 m)
Concentration of contaminants S0₂: < 0.5 ppm; H₂S: < 0.1 ppm; RH < 60% non-condensing
EN 60068-2-14, Test Nb, Temperature change 5° C to 55° C, 3° C/minute
EN 60068-2-27 Mechanical shock 15 G, 11 ms pulse, 6 shocks in each of 3 axis
EN 60068-2-6 Sinusoidal vibration Panel mount: 7.0 mm from 5 to 9 Hz; 2 G from 9 to 150 Hz DIN rail mount: 3.5 mm from 5 to 9 Hz; 1 G from 9 to 150 Hz 10 sweeps each axis, 1 octave/minute
EN 60529, IP20 Mechanical protection Protects against finger contact with high voltage as tested by standard probes. External protection is required for dust, dirt, water, and foreign objects of < 12.5 mm in diameter.
Electromagnetic Compatibility — Immunity per EN61000-6-2¹
EN 61000-4-2 Electrostatic discharge 8 kV air discharge to all surfaces and communications port, 4 kV contact discharge to exposed conductive surfaces
EN 61000-4-3 Radiated electromagnetic field 10 V/m from 80-1000 MHz, 80% AM at 1kHz 3 V/m from 1.4-2.0 GHz, 80% AM at 1kHz³ 1 V/m from 2.0-2.7 GHz, 80% AM at 1kHz³
EN 61000-4-4 Fast transient bursts 2 kV, 5 kHz with coupling network to AC and DC system power 2 kV, 5 kHz with coupling clamp to I/O 1 kV, 5 kHz with coupling clamp to communications
EN 61000-4-5 Surge immunity Power supply: 2 kV asymmetrical, 1 kV symmetrical I/O 1 kV symmetrical (24 VDC circuits require external surge protection)
EN 61000-4-6 Conducted disturbances 0.15 to 80 MHz, 10 V RMS, 80% AM at 1kHz
EN 61000-4-11 Voltage dips, short interruptions and voltage variations Residual voltage: 0% for 1 cycle, 40% for 12 cycles and 70% for 30 cycles @ 60Hz voltage jump at zero crossing
VDE 0160 Non-periodic overvoltage At 85 VAC line, 90° phase angle, apply 390 V peak, 1.3 ms pulse At 180 VAC line, 90° phase angle, apply 750 V peak, 1.3 ms pulse

394

Technical Specifications Appendix A

Table A-1 Technical S pecifications, continued

Electromagnetic Compatibility — Conducted and Radiated Emissions per EN 61000-6-3² and EN 61000-6-4
EN 55011, Class A, Group 1, conducted¹0.15 MHz to 0.5 MHz0.5 MHz to 5 MHz5 MHz to 30 MHz < 79 dB (μV) Quasi-peak; < 66 dB (μV) Average< 73 dB (μV) Quasi-peak; < 60 dB (μV) Average< 73 dB (μV) Quasi-peak; < 60 dB (μV) Average
EN 55011, Class A, Group 1, radiated¹30 MHz to 230 MHz230 MHz to 1 GHz 40 dB (μV/m) Quasi-peak; measured at 10 m47 dB (μV/m) Quasi-peak; measured at 10 m
EN 55011, Class B, Group 1, conducted²0.15 to 0.5 MHz0.5 MHz to 5 MHz5 MHz to 30 MHz < 66 dB (μV) Quasi-peak decreasing with log frequency to 56 dB (μV);< 56 dB (μV) Average decreasing with log frequency to 46 dB (μV)< 56 dB (μV) Quasi-peak; < 46 dB (μV) Average< 60 dB (μV) Quasi-peak; < 50 dB (μV) Average
EN 55011, Class B, Group 1, radiated²30 MHz to 230 kHz230 MHz to 1 GHz 30 dB (μV/m) Quasi-peak; measured at 10 m37 dB (μV/m) Quasi-peak; measured at 10 m
High Potential Isolation Test
24 V/5 V nominal circuits115/230 V circuits to ground115/230 V circuits to 115/230 V circuits115/230 V circuits to 24 V/5 V circuits 500 VAC (type test of optical isolation boundaries)1500 VAC routine test / 2500 VDC type test1500 VAC routine test / 2500 VDC type test1500 VAC routine test / 4242 VDC type test

1 Unit must be mounted on a grounded metallic frame with the S 7-200 ground connection made directly to the mounting metal. Cables are routed along metallic supports. 2 Unit must be mounted in a grounded metal enclosure. AC input power line must be equipped with a E P C O S B84115-E-A30 filter or equivalent, 25 cm max. wire length from filters to the S 7-200. The 24 VDC supply and sensor supply wiring must be shielded. 3 Requirements apply after J uly 2009

395

CPU Specifications

Table A-2 CPU Order Numbers

Order Number CPU Model Power Supply (Nominal) Digital Inputs Digital Outputs Comm Ports Analog Inputs Analog Outputs Removable Connector
6ES7 211-0AA23-0XB0 CPU 221 24 VDC 6 x 24 VDC 4 x 24 VDC 1 No No No
6ES7 211-0BA23-0XB0 CPU 221 120 to 240 VAC 6 x 24 VDC 4 x Relay 1 No No No
6ES7 212-1AB23-0XB0 CPU 222 24 VDC 8 x 24 VDC 6 x 24 VDC 1 No No No
6ES7 212-1BB23-0XB0 CPU 222 120 to 240 VAC 8 x 24 VDC 6 x Relay 1 No No No
6ES7 214-1AD23-0XB0 CPU 224 24 VDC 14 x 24 VDC 10 x 24 VDC 1 No No Yes
6ES7 214-1BD23-0XB0 CPU 224 120 to 240 VAC 14 x 24 VDC 10 x Relay 1 No No Yes
6ES7 214-2AD23-0XB0 CPU 224XP 24 VDC 14 x 24 VDC 10 x 24 VDC 2 2 1 Yes
6ES7 214-2AS23-0XB0 CPU 224XPsi 24 VDC 14 x 24 VDC 10 x 24 VDC 2 2 1 Yes
6ES7 214-2BD23-0XB0 CPU 224XP 120 to 240 VAC 14 x 24 VDC 10 x Relay 2 2 1 Yes
6ES7 216-2AD23-0XB0 CPU 226 24 VDC 24 x 24 VDC 16 x 24 VDC 2 No No Yes
6ES7 216-2BD23-0XB0 CPU 226 120 to 240 VAC 24 x 24 VDC 16 x Relay 2 No No Yes

Table A-3 CPU General Specifications

Order Number Module Name and Description Dimensions (mm) (W x H x D) Weight Dissipation VDC Available +5 VDC +24 VDC¹
6ES7 211-0AA23-0XB0 CPU 221 DC/DC/DC 6 Inputs/4 Outputs 90 x 80 x 62 270 g 3 W 0 mA 180 mA
6ES7 211-0BA23-0XB0 CPU 221 AC/DC/Relay 6 Inputs/4 Relays 90 x 80 x 62 310 g 6 W 0 mA 180 mA
6ES7 212-1AB23-0XB0 CPU 222 DC/DC/DC 8 Inputs/6 Outputs 90 x 80 x 62 270 g 5 W 340 mA 180 mA
6ES7 212-1BB23-0XB0 CPU 222 AC/DC/Relay 8 Inputs/6 Relays 90 x 80 x 62 310 g 7 W 340 mA 180 mA
6ES7 214-1AD23-0XB0 CPU 224 DC/DC/DC 14 Inputs/10 Outputs 120.5 x 80 x 62 360 g 7 W 660 mA 280 mA
6ES7 214-1BD23-0XB0 CPU 224 AC/DC/Relay14 Inputs/10 Relays 120.5 x 80 x 62 410 g 10 W 660 mA 280 mA
6ES7 214-2AD23-0XB0 CPU 224XP DC/DC/DC 14 Inputs/10 Outputs 140 x 80 x 62 390 g 8 W 660 mA 280 mA
6ES7 214-2AS23-0XB0 CPU 224XPsi DC/DC/DC 14 Inputs/10 Outputs 140 x 80 x 62 390 g 8 W 660 mA 280 mA
6ES7 214-2BD23-0XB0 CPU 224XP AC/DC/Relay 14 Inputs/10 Relays 140 x 80 x 62 440 g 11 W 660 mA 280 mA
6ES7 216-2AD23-0XB0 CPU 226 DC/DC/DC 24 Inputs/16 Outputs 196 x 80 x 62 550 g 11 W 1000 mA 400 mA
6ES7 216-2BD23-0XB0 CPU 226 AC/DC/Relay 24 Inputs/16 Relays 196 x 80 x 62 660 g 17 W 1000 mA 400 mA

¹ This is the 24 VDC sensor power that is available after the internal relay coil power and 24 VDC comm port power requirements have been accounted for.

396

Technical Specifications Appendix A

Table A-4 CPU S specifications

CPU 221 CPU 222 CPU 224 CPU 224XP CPU 224XPsi CPU 226
Memory
User program size with run mode edit without run mode edit 4096 bytes 4096 bytes 8192 bytes 12288 bytes 12288 bytes 16384 bytes 16384 bytes 24576 bytes
User data 2048 bytes 8192 bytes 10240 bytes 10240 bytes
Backup (super cap) (optional battery) 50 hours typical (8 hours min. at □□°C) 200 days typical 100 hours typical (70 hours min. at 40°C) 200 days typical 100 hours typical (70 hours min. at 40°C) 200 days typical 100 hours typical (70 hours min. at 40°C) 200 days typical
I/O
Digital I/O 6 inputs/4 outputs 8 inputs/6 outputs 14 inputs/10 outputs 14 inputs/10 outputs 24 inputs/16 outputs
Analog I/O none 2 inputs/1 output none
Digital I/O image size 256 (128 In/128 Out)
Analog I/O image size None 32 (16 In/16 Out) 64 (32 In/32 Out)
Max. expansion modules allowed None 2 modules¹ 7 modules¹
Max. intelligent modules allowed None 2 modules¹ 7 modules¹
Pulse Catch inputs 6 8 14 24
High-Speed Counters Single phase Two phase 4 counters total 4 at 30 kHz 2 at 20 kHz 6 counters total 6 at 30 kHz 4 at 20 kHz 6 counters total 4 at 30 kHz 2 at 200 kHz 3 at 20 kHz 1 at 100 kHz 6 counters total 6 at 30 kHz 4 at 20 kHz
Pulse outputs 2 at 20 kHz (DC outputs only) 2 at 100 kHz (DC outputs only) 2 at 20 kHz (DC outputs only)
General
Timers 256 total timers; 4 timers (1 ms); 16 timers (10 ms); 236 timers (100 ms)
Counters 256 (backed by super capacitor or battery)
Internal memory bits Stored on power down 256 (backed by super capacitor or battery) 112 (stored to EEPROM)
Timed interrupts 2 with 1 ms resolution
Edge interrupts 4 up and/or 4 down
Analog adjustment 1 with 8 bit resolution 2 with 8 bit resolution
Boolean execution speed 0.22 µs per instruction
Real Time Clock Optional cartridge Built-in
Cartridge options Memory, Battery, and Real Time Clock Memory and battery
Communications Built-in
Ports (Limited Power) 1 RS-485 port 2 RS-485 ports
PPI, MPI (slave) baud rates 9.6, 19.2, 187.5 kbaud
Freeport baud rates 1.2 kbaud to 115.2 kbaud
Max. cable length per segment With isolated repeater: 1000 m up to 187.5 kbaud, 1200 m up to 38.4 kbaud Without isolated repeater: 50 m
Max. number of stations 32 per segment, 126 per network
Max. number of masters 32
Peer to Peer (PPI Master Mode) Yes (NETR/NETW)
MPI connections 4 total, 2 reserved (1 for a PG and 1 for an OP)

¹ You must calculate your power budget to determine how much power (or current) the S 7-200 CPU can provide for your configuration. If the CPU power budget is exceeded, you may not be able to connect the maximum number of modules. See Appendix A for CPU and expansion module power requirements, and Appendix B to calculate your power budget.

397

Table A-5 CPU Power Specifications

DC AC
Input Power
Input voltage 20.4 to 28.8 VDC 85 to 264 VAC (47 to 63 Hz)
Input current CPU only at 24 VDC Max. load at 24 VDC CPU only Max. load
CPU 221 80 mA 450 mA 30/15 mA at □□□/□□□ VAC 120/60 mA at 120/240 VAC
CPU 222 85 mA 500 mA 40/20 mA at 120/240 VAC 140/70 mA at 120/240 VAC
CPU 224 110 mA 700 mA 60/30 mA at 120/240 VAC 200/100 mA at 120/240VAC
CPU 224XP 120 mA 900 mA 70/35 mA at 120/240 VAC 220/100 mA at 120/240 VAC
CPU 224XPsi 120 mA 900 mA - -
CPU 226 150 mA 1050 mA 80/40 mA at 120/240 VAC 320/160 mA at 120/240VAC
Inrush current 12 A at 28.8 VDC 20 A at 264 VAC
Isolation (field to logic) Not isolated 1500 VAC
Hold up time (loss of power) 10 ms at 24 VDC 20/80 ms at 120/240 VAC
Fuse (non-replaceable) 3 A, 250 V Slow Blow 2 A, 250 V Slow Blow
24 VDC Sensor Power
Sensor voltage (Limited Power) L+ minus 5 V 20.4 to 28.8 VDC
Current limit 1.5 A peak, thermal limit non-destructive (See Table A-3 for rated load.)
Ripple noise Derived from input power Less than 1 V peak-to-peak
Isolation (sensor to logic) Not isolated

Table A-6 CPU Digital Input Specifications

General 24 VDC Input (CPU 221, CPU 222, CPU 224, CPU 226) 24 VDC Input (CPU 224XP, CPU 224XPsi)
Type Sink/Source (IEC Type 1 Sink) Sink/Source (IEC Type 1 Sink, except I0.3 to I0.5)
Rated voltage 24 VDC at 4 mA typical 24 VDC at 4 mA typical
Max. continuous permissible voltage 30 VDC
Surge voltage 35 VDC for 0.5 s
Logic 1 (min.) 15 VDC at 2.5 mA 15 VDC at 2.5 mA (I0.0 to I0.2 and I0.6 to I1.5)
4 VDC at 8 mA (I0.3 to I0.5)
Logic 0 (max.) 5 VDC at 1 mA 5 VDC at 1 mA (I0.0 to I0.2 and I0.6 to I1.5)
1 VDC at 1 mA (I0.3 to I0.5)
Input delay Selectable (0.2 to 12.8 ms)
Connection of 2 wire proximity sensor (Bero)
Permissible leakage current (max.) 1 mA
Isolation (field to logic) Yes
Optical (galvanic) 500 VAC for 1 minute
Isolation groups See wiring diagram
High Speed Counter (HSC) input rate
HSC Inputs Logic 1 Level Single phase Two phase
All HSC 15 to 30 VDC 20 kHz 10 kHz
All HSC 15 to 26 VDC 30 kHz 20 kHz
HC4, HC5 on CPU 224XP and CPU 224XPsi only > 4 VDC 200 kHz 100 kHz
Inputs on simultaneously All All
CPU 224XP AC/DC/RELAY only:
All at 55° C with DC inputs at 26 VDC max.
All at 50° C with DC inputs at 30 VDC max.
Cable length (max.)
Shielded 500 m normal inputs, 50 m HSC inputs¹
Unshielded 300 m normal inputs

¹ Shielded twisted pair is recommended for HSC inputs.

398

Technical Specifications Appendix A

Table A-7 CPU Digital Output S pecifications

General 24 VDC Output (CPU 221, CPU 222, CPU 224, CPU 226) 24 VDC Output (CPU 224XP) 24 VDC Output (CPU 224XPsi) Relay Output
Type Solid State-MOSFET (Sourcing) Solid State-MOSFET (Sinking) Dry contact
Rated voltage 24 VDC 24 VDC 24 VDC 24 VDC or 250 VAC
Voltage range 20.4 to 28.8 VDC 5 to 28.8 VDC (Q0.0 to Q0.4) 20.4 to 28.8 VDC (Q0.5 to Q1.1) 5 to 28.8 VDC 5 to 30 VDC or 5 to 250 VAC
Surge current (max.) 8 A for 100 ms 5 A for 4 s @ 10% duty cycle
Logic 1 (min.) 20 VDC at maximum current L+ minus 0.4 V at max. current External Voltage Rail minus 0.4V with 10K pullup to External Voltage Rail -
Logic 0 (max.) 0.1 VDC with 10 K Ω Load 1M + 0.4V at max. load -
Rated current per point (max.) 0.75 A 2.0 A
Rated current per common (max.) 6 A 3.75 A 7.5 A 10 A
Leakage current (max.) 10 μA -
Lamp load (max.) 5 W 30 W DC; 200 W AC²,³
Inductive clamp voltage L+ minus 48 VDC, 1 W dissipation 1M +48 VDC, 1 W dissipation -
On State resistance (contact) 0.3 Ω typical (0.6 Ω max.) 0.2 Ω (max. when new)
Isolation Optical (galvanic, field to logic) Logic to contact Resistance (logic to contact) Isolation groups 500 VAC for 1 minute - - See wiring diagram - 1500 VAC for 1 minute 100 M Ω See wiring diagram
Delay (max.) Off to on (μs) On to off (μs) Switching 2μs (Q0.0, Q0.1), 15μs (all other) 10μs (Q0.0, Q0.1), 130μs (all other) - 0.5μs (Q0.0, Q0.1), 15μs (all other) 1.5μs (Q0.0, Q0.1), 130μs (all other) - - - 10 ms
Pulse frequency (max.) 20 kHz¹ (Q0.0 and Q0.1) 100 kHz¹ (Q0.0 and Q0.1) 100 kHz¹ (Q0.0 and Q0.1) 1 Hz
Lifetime mechanical cycles - - - 10,000,000 (no load)
Lifetime contacts - - - 100,000 (rated load)
Outputs on simultaneously All at 55° C (horizontal), All at 45° C (vertical)
Connecting two outputs in parallel Yes, only outputs in same group No
Cable length (max.) Shielded Unshielded 500 m 150 m

¹ Depending on your pulse receiver and cable, an additional external load resistor (at least 10% of rated current) may improve pulse signal quality and noise immunity.

² Relay lifetime with a lamp load will be reduced by 75% unless steps are taken to reduce the turn-on surge below the surge current rating of the output.

³ Lamp load wattage rating is for rated voltage. Reduce the wattage rating proportionally for voltage being switched (for example 120 VAC - 100 W).

Warning

When a mechanical contact turns on output power to the S7-200 CPU, or any digital expansion module, it sends a “1” signal to the digital outputs for approximately 50 microseconds.

This could cause unexpected machine or process operation which could result in death or serious injury to personnel, and/or damage to equipment.

You must plan for this, especially if you are using devices which respond to short duration pulses.

399

Table A-8 CPU 224XP and CPU 224XPsi Analog Input Specifications

\begin{tabular}{|l|l|} \hline General & Analog Input (CPU 224XP, CPU 224XPsi) \ \hline Number of Inputs & 2 points \ \hline Analog input type & Single-ended \ \hline Voltage range & ±10 V \ \hline Data word format, full scale range & -32,000 to +32,000 \ \hline DC Input impedance & > 100 K\Omega \ \hline Maximum input voltage & 30 VDC \ \hline Resolution & 11 bits plus 1 sign bit \ \hline LSB value & 4.88 mV \ \hline Isolation & None \ \hline Accuracy$^1$ & \ \quad Worst case 0° to 55° C & ±2.5% of full scale \ \quad Typical 25° C & ±1.0% of full scale \ \hline Repeatability & ±0.05% of full scale \ \hline Analog to digital conversion time & 125 msec \ \hline Conversion type & Sigma Delta \ \hline Step response & 250 ms max. \ \hline Noise rejection & -20 dB @ 50 Hz typical \ \hline \end{tabular}

$^1$ Analog input accuracy may deviate up to +/-10% of full scale when subjected to severe RF interferences such as specified in the product standard EN 61131-2:2007.

Table A-9 CPU 224XP and CPU 224XPsi Analog Output Specifications

\begin{tabular}{|l|l|} \hline General & Analog Output (CPU 224XP, CPU 224XPsi) \ \hline Number of outputs & 1 point \ \hline Signal range & \ \quad Voltage & 0 to 10 V (Limited Power) \ \quad Current & 0 to 20 mA (Limited Power) \ \hline Data word format, full range & 0 to +32767 \ \hline Date word format, full scale & 0 to +32000 \ \hline Resolution, full range & 12 bits \ \hline LSB value & \ \quad Voltage & 2.44 mV \ \quad Current & 4.88 \muA \ \hline Isolation & none \ \hline Accuracy & \ \quad Worst case, 0° to 55° C & \ \qquad Voltage output & ± 2% of full-scale \ \qquad Current output & ± 3% of full-scale \ \quad Typical 25° C & \ \qquad Voltage output & ± 1% of full-scale \ \qquad Current output & ± 1% of full-scale \ \hline Settling time & \ \quad Voltage output & < 50 \muS \ \quad Current output & < 100 \muS \ \hline Maximum output drive & \ \quad Voltage output & ≥ 5000 \Omega minimum \ \quad Current output & ≤ 500 \Omega maximum \ \hline \end{tabular}

400

Technical Specifications Appendix A

Wiring Diagrams

Figure from the manual Figure A-2 CPU Inputs and Outputs

Figure from the manual Figure A-3 CPU 221 Wiring Diagrams

401

Figure from the manual CPU 222 DC/DC/DC (6ES7 212-1AB23-0XB0) 24 VDC Power

M L+ 0.0 0.1 0.2 0.3 0.4 0.5 • ⏚ M L+ DC 1M 0.0 0.1 0.2 0.3 2M 0.4 0.5 0.6 0.7 M L+

24 VDC Sensor Power Output

CPU 222 AC/DC/Relay (6ES7 212-1BB23-0XB0) 120/240 VAC Power

N(-) L(+) N(-) L(+)

1L 0.0 0.1 0.2 • 2L 0.3 0.4 0.5 ⏚ N L1 AC 1M 0.0 0.1 0.2 0.3 2M 0.4 0.5 0.6 0.7 M L+

24 VDC Sensor Power Output

CPU 224 DC/DC/DC (6ES7 214-1AD23-0XB0) 24 VDC Power

1M 1L+ 0.0 0.1 0.2 0.3 0.4 2M 2L+ 0.5 0.6 0.7 1.0 1.1 • ⏚ M L+ DC 1M 0.0 0.1 0.2 0.3 0.4 0.5 0.6 0.7 2M 1.0 1.1 1.2 1.3 1.4 1.5 M L+

24 VDC Sensor Power Output

CPU 224 AC/DC/Relay (6ES7 214-1BD23-0XB0) 120/240 VAC Power

N(-) L(+) N(-) L(+) N(-) L(+)

1L 0.0 0.1 0.2 0.3 • 2L 0.4 0.5 0.6 • 3L 0.7 1.0 1.1 ⏚ N L1 AC 1M 0.0 0.1 0.2 0.3 0.4 0.5 0.6 0.7 2M 1.0 1.1 1.2 1.3 1.4 1.5 M L+

24 VDC Sensor Power Output

Figure A-4 CPU 222 and CPU 224 Wiring Diagrams

402

Technical Specifications Appendix A

Figure from the manual CPU 224XP Analog I/O CPU 224XP DC/DC/DC (6ES7 214-2AD23-0XB0) 24 VDC Power M I V M A+ B+ 1M 1L+ 0.0 0.1 0.2 0.3 0.4 2M 2L+ 0.5 0.6 0.7 1.0 1.1 • ⏚ M L+ DC 1M 0.0 0.1 0.2 0.3 0.4 0.5 0.6 0.7 2M 1.0 1.1 1.2 1.3 1.4 1.5 M L+ 24 VDC Sensor Power Output

CPU 224XPsi Analog I/O CPU 224XPsi DC/DC/DC (6ES7 214-2AS23-0XB0) 24 VDC Power M I V M A+ B+ 1M • 0.0 0.1 0.2 0.3 0.4 • • 0.5 0.6 0.7 1.0 1.1 • ⏚ M L+ DC 1M 0.0 0.1 0.2 0.3 0.4 0.5 0.6 0.7 2M 1.0 1.1 1.2 1.3 1.4 1.5 M L+ 24 VDC Sensor Power Output

CPU 224XP Analog I/O CPU 224XP AC/DC/Relay (6ES7 214-2BD23-0XB0) 120/240 VAC Power N(-) L(+) N(-) L(+) N(-) L(+) M I V M A+ B+ 1L 0.0 0.1 0.2 0.3 • 2L 0.4 0.5 0.6 • 3L 0.7 1.0 1.1 ⏚ N L1 AC 1M 0.0 0.1 0.2 0.3 0.4 0.5 0.6 0.7 2M 1.0 1.1 1.2 1.3 1.4 1.5 M L+ 24 VDC Sensor Power Output

Figure A-5 CPU 224XP Wiring Diagrams

403

Figure from the manual

Figure A-6 CPU 226 Wiring Diagrams

Table A-10 Pin Assignments for the S7-200 Communications Port (Limited Power)

Connector Pin Number PROFIBUS Signal Port 0/Port 1
Pin 1Pin 5 1 S shield Chassis ground
2 24 V Return Logic common
3 RS-485 Signal B RS-485 Signal B
4 Request-to-Send RTS (TTL)
5 5 V Return Logic common
6 +5 V +5 V, 100 Ω series resistor
7 +24 V +24 V
8 RS-485 Signal A RS-485 Signal A
9 Not applicable 10-bit protocol select (input)
Connector shell S shield Chassis ground

404

Technical Specifications Appendix A

Digital Expansion Modules Specifications

Table A-11 Digital Expansion Modules Order Numbers

Order Number Expansion Model Digital Inputs Digital Outputs Removable Connector
6ES7 221-1BF22-0XA0 EM 221 Digital Input 8 x 24 VDC 8 x 24 VDC - Yes
6ES7 221-1EF22-0XA0 EM 221 Digital Input 8 x 120/230 VAC 8 x 120/230 VAC - Yes
6ES7 221-1BH22-0XA0 EM 221 Digital Input 16 x 24 VDC 16 x 24 VDC - Yes
6ES7 222-1BD22-0XA0 EM 222 Digital Output 4 x 24 VDC -5A - 4 x 24 VDC -5A Yes
6ES7 222-1HD22-0XA0 EM 222 Digital Output 4 x Relays-10A - 4 x Relay-10A Yes
6ES7 222-1BF22-0XA0 EM 222 Digital Output 8 x 24 VDC - 8 x 24 VDC -0.75A Yes
6ES7 222-1HF22-0XA0 EM 222 Digital Output 8 x Relays - 8 x Relay-2A Yes
6ES7 222-1EF22-0XA0 EM 222 Digital Output 8 x 120/230 VAC - 8 x 120/230 VAC Yes
6ES7 223-1BF22-0XA0 EM 223 24 VDC Digital Comb 4 Inputs/4 Outputs 4 x 24 VDC 4 x 24 VDC -0.75A Yes
6ES7 223-1HF22-0XA0 EM 223 24 VDC Digital Comb 4 Inputs/4 Relay Outputs 4 x 24 VDC 4 x Relay-2A Yes
6ES7 223-1BH22-0XA0 EM 223 24 VDC Digital Comb 8 Inputs/8 Outputs 8 x 24 VDC 8 x 24 VDC -0.75A Yes
6ES7 223-1PH22-0XA0 EM 223 24 VDC Digital Comb 8 Inputs/8 Relay Outputs 8 x 24 VDC 8 x Relay-2A Yes
6ES7 223-1BL22-0XA0 EM 223 24 VDC Digital Comb 16 Inputs/16 Outputs 16 x 24 VDC 16 x 24 VDC -0.75A Yes
6ES7 223-1PL22-0XA0 EM 223 24 VDC Digital Comb 16 Inputs/16 Relay Outputs 16 x 24 VDC 16 x Relay-2A Yes
6ES7 223-1BM22-0XA0 EM 223 24 VDC Digital Comb 32 Inputs/32 Outputs 32 x 24 VDC 32 x 24 VDC -0.75 A Yes
6ES7 223-1PM22-0XA0 EM 223 24 VDC Digital Comb 32 Inputs/32 Relay Outputs 32 x 24 VDC 32 x Relay-2 A Yes

Table A-12 Digital Expansion Modules General Specifications

Order Number Module Name and Description Dimensions (mm) (W x H x D) Weight Dissipation VDC Requirements +5 VDC +24 VDC
6ES7 221-1BF22-0XA0 EM 221 DI 8 x 24 VDC 46 x 80 x 62 150 g 2 W 30 mA ON: 4 mA/input
6ES7 221-1EF22-0XA0 EM 221 DI 8 x 120/230 VAC 71.2 x 80 x 62 160 g 3 W 30 mA -
6ES7 221-1BH22-0XA0 EM 221 DI 16 x 24 VDC 71.2 x 80 x 62 160 g 3 W 70 mA ON: 4 mA/input
6ES7 222-1BD22-0XA0 EM 222 DO 4 x 24 VDC -5A 46 x 80 x 62 120 g 3 W 40 mA -
6ES7 222-1HD22-0XA0 EM 222 DO 4 x Relays-10A 46 x 80 x 62 150 g 4 W 30 mA ON: 20 mA/output
6ES7 222-1BF22-0XA0 EM 222 DO 8 x 24 VDC 46 x 80 x 62 150 g 2 W 50 mA -
6ES7 222-1HF22-0XA0 EM 222 DO 8 x Relays 46 x 80 x 62 170 g 2 W 40 mA ON: 9 mA/output
6ES7 222-1EF22-0XA0 EM 222 DO 8 x 120/230 VAC 71.2 x 80 x 62 165 g 4 W 110 mA -
6ES7 223-1BF22-0XA0 EM 223 24 VDC 4 In/4 Out 46 x 80 x 62 160 g 2 W 40 mA ON: 4 mA/input
6ES7 223-1HF22-0XA0 EM 223 24 VDC 4 In/4 Relays 46 x 80 x 62 170 g 2 W 40 mA ON: 9 mA/output, 4 mA/input
6ES7 223-1BH22-0AX0 EM 223 24 VDC 8 In/8 Out 71.2 x 80 x 62 200 g 3 W 80 mA ON: 4 mA/input
6ES7 223-1PH22-0XA0 EM 223 24 VDC 8 In/8 Relays 71.2 x 80 x 62 300 g 3 W 80 mA ON: 9 mA/output, 4 mA/input
6ES7 223-1BL22-0XA0 EM 223 24 VDC 16 In/16 Out 137.3 x 80 x 62 360 g 6 W 160 mA ON: 4 mA/input
6ES7 223-1PL22-0XA0 EM 223 24 VDC 16 In/16 Relays 137.3 x 80 x 62 400 g 6 W 150 mA ON: 9 mA/output, 4 mA/input
6ES7 223-1BM22-0XA0 EM 223 24 VDC 32 In/32 Out 196 x 80 x 62 500 g 9 W 240 mA ON: 4 mA/input
6ES7 223-1PM22-0XA0 EM 223 24 VDC 32 In/32 Relay 196 x 80 x 62 580 g 13 W 205 mA ON: 9 mA/output 4 mA/input

405

Table A-13 Digital Expansion Modules Input Specifications

General 24 VDC Input 120/230 VAC Input (47 to 63 HZ)
Type Sink/Source (IEC Type 1 sink) IEC Type I
Rated voltage 24 VDC at 4 mA 120 VAC at 6 mA or 230 VAC at 9 mA nominal
Maximum continuous permissible voltage 30 VDC 264 VAC
Surge voltage (max.) 35 VDC for 0.5 s -
Logic 1 (min.) 15 VDC at 2.5 mA 79 VAC at 2.5 mA
Logic 0 (max.) 5 VDC at 1 mA 20 VAC or 1 mA AC
Input delay (max.) 4.5 ms 15 ms
Connection of 2 wire proximity sensor (Bero)
Permissible leakage current (max.) 1 mA 1 mA AC
Isolation
Optical (galvanic, field to logic) 500 VAC for 1 minute 1500 VAC for 1 minute
Isolation groups See wiring diagram 1 point
Inputs on simultaneously All at 55° C (horizontal), All on at 45° C (vertical)
Cable length (max.)
Shielded 500 m 500 m
Unshielded 300 m 300 m

Figure from the manual

Figure A-7 S7-200 Digital Expansion Modules Inputs

406

Figure from the manual

Figure from the manual

Technical Specifications Appendix A

Table A-14 Digital Expansion Modules Output Specifications

General 24 VDC Output Relay Output 120/230 VAC Output
0.75 A 5 A 2 A 10 A
Type Solid state-MOSFET (Sourcing) Dry contact Triac, zero-cross turn-on
Rated voltage 24 VDC 24 VDC or 250 VAC 120/230 VAC
Voltage range 20.4 to 28.8 VDC 5 to 30 VDC or 5 to 250 VAC 12 to 30 VDC or 12 to 250 VAC 40 to 264 VAC (47 to 63 Hz)
24 VDC coil power voltage range - 20.4 to 28.8 VDC -
Surge current (max.) 8 A for 100 ms 30 A 5 A for 4 s @ 10% duty cycle 15 A for 4 s @ 10% duty cycle 5 A rms for 2 AC cycles
Logic 1 (min.) 20 VDC - L1 (-0.9 V rms)
Logic 0 (max.) 0.1 VDC with 10 K Ω Load 0.2 VDC with 5 K Ω Load - -
Rated current per point (max.) 0.75 A 5 A 2.00 A 10 A resistive; 2 A DC inductive; 3 A AC inductive 0.5 A AC¹
Rated current per common (max.) 10 A 5 A 10 A 10 A 0.5 A AC
Leakage current (max.) 10 μA 30 μA - 1.1 mA rms at 132 VAC and 1.8 mA rms at 264 VAC
Lamp load (max.) 5 W 50 W 30 W DC/ 200 W AC⁴,⁵ 100 W DC/ 1000 W AC 60 W
Inductive clamp voltage L+ minus 48 V L+ minus 47 V² - -
On state resistance (contact) 0.3 Ω typical (0.6 Ω max.) 0.05 Ω max. 0.2 Ω max. when new 0.1 Ω max. when new 410 Ω max. when load current is less than 0.05A
Isolation
Optical (galvanic, field to logic) 500 VAC for 1 minute - 1500 VAC for 1 minute
Coil to logic - None -
Coil to contact - 1500 VAC for 1 minute -
Resistance (coil to contact) - 100 M Ω min. when new -
Isolation groups See wiring diagram See wiring diagram 1 point
Delay Off to On/On to Off (max.) 50 μs / 200 μs 500 μs - - 0.2 ms + 1/2 AC cycle
Switching (max.) - - 10 ms 15 ms -
Switching frequency (max.) - 1 Hz 10 Hz
Lifetime mechanical cycles - 10,000,000 (no load) 30,000,000 (no load) -
Lifetime contacts - 100,000 (rated load) 30,000 (rated load) -
Output on simultaneously All at 55° C (horizontal), All at 45° C (vertical) All at 55 °C (horizontal) with 20A max. module current. All at 45°C (vertical) with 20A max. module current⁵. All at 40 °C (horizontal) with 10A per point All at 55° C (horizontal), All at 45° C (vertical)
Connecting two outputs in parallel Yes, only outputs in same group No No
Cable length (max.)
Shielded 500 m 500 m 500 m
Unshielded 150 m 150 m 150 m

1 Load current must be full wave AC and must not be half-wave because of the zero-cross circuitry. Minimum load current is 0.05 A AC. With a load current between 5 mA and 50 mA AC, the current can be controlled, but there is an additional voltage drop due to series resistance of 410 Ohms.

2 If the output overheats due to excessive inductive switching or abnormal conditions, the output point may turn off or be damaged. The output could overheat or be damaged if the output is subjected to more than 0.7 J of energy switching an inductive load off. To eliminate the need for this limitation, a suppression circuit as described in Chapter 3 can be added in parallel with the load. These components need to be sized properly for the given application.

3 The EM 222 DO 4 x Relay has a different FM rating than the rest of the S7-200. This module has a T4 rating, instead of T4A for FM Class I, Division Groups A, B, C, and D Hazardous Locations.

4 Relay lifetime with a lamp load will be reduced by 75% unless steps are taken to reduce the turn-on surge below the surge current rating of the output.

5 Lamp load wattage rating is for rated voltage. Reduce the wattage rating proportionally for voltage being switched (for example 120 VAC - 100 W).

Figure from the manual

Warning

When a mechanical contact turns on output power to the S7-200 CPU, or any digital expansion module, it sends a “1” signal to the digital outputs for approximately 50 microseconds.

This could cause unexpected machine or process operation which could result in death or serious injury to personnel, and/or damage to equipment.

You must plan for this, especially if you are using devices which respond to short duration pulses.

407

Figure from the manual Figure A-8 S7-200 Digital Expansion Modules Outputs

Wiring Diagrams

Figure from the manual Figure A-9 Wiring Diagrams for EM 222 and EM 223 Expansion Modules

408

Figure from the manual

Figure from the manual

Technical Specifications Appendix A

Figure from the manual EM 221 Digital Input 8 x 24 VDC (6ES7 221-1BF22-0XA0)

● ● 1M .0 .1 .2 .3 ⊣ ● 2M .4 .5 .6 .7

EM 221 Digital Input 16 x 24 VDC (6ES7 221-1BH22-0XA0)

● ● 1M .0 .1 .2 .3 2M .4 .5 .6 .7 ⊣ ● 3M .0 .1 .2 .3 4M .4 .5 .6 .7

EM 221 Digital Input 8 x AC 120/230 V (6ES7 221-1EF22-0XA0)

0N 0N .0 1N 1N .1 2N 2N .2 3N 3N .3 ⊣ 4N .4 5N 5N .5 6N 6N .6 7N 7N .7

EM 222 Digital Output 8 x AC 120/230 V (6ES7 222-1EF22-0AX0)

N L1 0L 0L .0 1L 1L .1 2L 2L .2 3L 3L .3 ⊣ 4L .4 5L 5L .5 6L 6L .6 7L 7L .7

EM 222 Digital Output 8 x 24 VDC (6ES7 222-1BF22-0XA0)

● 1M 1L+ .0 .1 .2 .3 ⊣ 2M 2L+ .4 .5 .6 .7

EM 222 Digital Output 8 x Relays (6ES7 222 1HF22-0XA0)

N(-) L(+) ⊣ ● 1L .0 .1 .2 .3 M L+ 2L .4 .5 .6 .7 24 VDC Coil + power L (+) N (-)

EM 222 Digital Output 4 x 24 VDC -5A (6ES7 222-1BD22-0XA0)

● 0M 0L+ .0 1M 1L+ .1 ⊣ 2M 2L+ .2 3M 3L+ .3

Figure A-10 Wiring Diagrams for EM 221 and EM 222 Expansion Modules

409

EM 223 24 VDC Digital Combination 8 Inputs/8 Outputs (6ES7 223-1BH22-0XA0)

Figure from the manual

EM 223 24 VDC Digital Combination 8 Inputs/8 Relay Out- puts (6ES7 223-1PH22-0XA0)

EM 223 24 VDC Digital Combination 16 Inputs/16 Outputs (6ES7 223-1BL22-0XA0)

EM 223 24 VDC Digital Combination 16 Inputs/16 Relay Outputs (6ES7 223-1PL22-0XA0)

Figure A-11 Wiring Diagrams for EM 223 Expansion Modules

410